Have had the fridge since August. It does not say watts. Its Haier brand volt 115. rated current 1.4 A. rated freq 60 hz.
As Dennis said, 161 watts
when running. The startup wattage, which may last only a few seconds, but is important as well, may be 500-900 watts, so make sure that your inverter has at least a 1000 watt rating, unless you know the startup wattage needed. Knowing that the startup surge demand is short, we can drop it from the solar power calculations as long as the inverter has the overhead.
So, we know that we need at least 161 when on, and that comes from the 115V * 1.4A. Now, if we take that same wattage and factor it against a 12.8V system (the input of the inverter), we get 12.578125 Amps (161W / 12.8V). So, as long as we can provide at least 13 amps (let's give the inverter something to work with as inefficiency), then we know that we can keep the fridge running when it needs to run.
Now we just have to figure out how many hours a day the fridge is running, versus how many hours the fridge is off. Most of my fridges in "normal" temperature rooms run for about 15-20 minutes an hour, or a duty cycle (on vs. off time ratio) of between .25 (15 min) and .33 (20 minutes), and when the weather gets hot, .5 (30 minutes). So, out of 24 hours a day, the fridge is on between 6 and 8 hours, and as many as 12 hours in the heat.
Now that we know that, and the wattage it needs when on, we can calculate the total watthours per day that the fridge is going to draw.
.25dutycycle * 24hours * 161Watts = 966WH (WattHours a day)
.33dutycycle * 24hours * 161Watts = 1,288WH (WattHours a day)
.5dutycycle * 24hours * 161Watts = 1,932WH (WattHours a day)
We now know that the fridge is going to need between 966WH and 1,288WH, with a maximum of 1,932WH when the temperature gets high. This means that we will need a battery bank capable of supplying at least that much power in
usable capacity
per sunny day. So if you take the worst case figure (1932WH) and divide by 12.8V, you get around 150AH. And if you live where it never really gets "hot", then you could go with the lower figure of 1,288WH, which is about 100.6AH. That is the needed "usable" capacity.
Now, that means that if we have clouds every other day, we need to double our battery bank's capacity. PLUS, batteries are rated in TOTAL CAPACITY, now USABLE CAPACITY. If you use a battery so that it provides it's total capacity (rated AH on battery), it will be at 0% SOC (State of Charge) and will not last but a few cycles of that use. Batteries like to be discharged slightly and then recharged soon afterwards, not sucked dry and left for a few days. Standard "Wet Cell" "Deep Cycle" batteries can be discharged 20% of rated (total capacity). This means that you can safely use 20AH from a 100AH Wet Cell battery (leaving 80AH still in the battery) without really hurting it (you should get thousands of good cycles). With AGM batteries, you can discharge it up to 50%, (50%SOC), leaving 50AH left in the battery from a 100AH rated battery. What these two factors mean together is that if we have clouds every other day, AND are using Wet Cell batteries, that 100.6AH to 150AH of needed "usable" capacity, now represents (100.6AH / .2 * 2)=1,006AH to (150 / .2 * 2)=1,500AH of rated total capacity. The .2 represents 20% discharge and the 2 is to calculate the doubling of the every other cloudy day. A 1,500AH battery pack can easily be built using a string of 30 Golf Cart batteries (205AH rated "total" capacity), hooked up in 15 parallel pairs of two batteries in series each. Each battery is going to run about $70 each, so the pack is going to end up costing you about $2,100.
This also means that you will need at least 150AH(what the fridge actually needs per day) * 14.4V (Charging voltage for Wet Cells to cover overhead of charging needed) = 2,160WH per day of actual solar charging power. If you get 5 hours of good strong sun a day, then that could be provided by 2,160WH / 5hours = 432W (minimum) of panels. If you only get three hours of good strong sun, then you would need 720W of panels (minimum).
Now, if you have less cloudy days, or your fridge is less power hungry than noted, then the number of panels needed will go down. If you go either the AC with inverter route, or the DC cooler version, INSULATE the unit real well with extra insulation, since a BTU wasted is wattage wasted.
Loup